Post by programmes1 on Nov 7, 2007 21:17:40 GMT
Whilst travelling on Valley lines today noticed some of the signals Grange Town area have had their heads changed so instead of 3 aspects only 1 capable of showing all aspects LED, my question is will LU ever do this or have they already done so?
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Nov 7, 2007 22:38:47 GMT
That sounds like a NR LED signal to me... I have no route knowledge of that area so I have no idea if it belongs to LU or NR
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Nov 7, 2007 23:22:16 GMT
from what i have seen and heard about LED's in signal heads on LUL it will be only allowed if the LED's was a direct replacement for a bulb (like the type in plat repeaters) the ones you are referring too are very big and have lots of ultra bright LED's and there is concern about them being too bright especially down the tunnels plus for us it will be the end to the nice easy relamp jobs we get
|
|
mrfs42
71E25683904T 172E6538094T
Big Hair Day
Posts: 5,922
|
Post by mrfs42 on Nov 7, 2007 23:50:42 GMT
from what i have seen and heard about LED's in signal heads on LUL it will be only allowed if the LED's was a direct replacement for a bulb (like the type in plat repeaters) I think that's unlikely (though stand corrected on this) there would need to be a lot of work done in development to ensure that the LED cluster and the inner/outer fresnel doublets are compatible. the ones you are referring too are very big and have lots of ultra bright LED's and there is concern about them being too bright especially down the tunnels I think that there would be a lot of discussion about making more signals approach lit at red - and changing the sighting lines of heads if you're going to go for the 'searchlight' option in tunnel. Having said that I can see a case for making normally GR 'down' signals LED on the most restrictive aspect and conversely those with the GR (usually) 'up' LED on whatever flavour of 'proceed' - however the use of two different (and both efficient in their own way) lighting systems may cause a lot of coughing amonst certain quarters. plus for us it will be the end to the nice easy relamp jobs we get But think of all the hours involved in re-sighting signals.......
|
|
|
Post by railtechnician on Nov 8, 2007 1:23:09 GMT
from what i have seen and heard about LED's in signal heads on LUL it will be only allowed if the LED's was a direct replacement for a bulb (like the type in plat repeaters) the ones you are referring too are very big and have lots of ultra bright LED's and there is concern about them being too bright especially down the tunnels plus for us it will be the end to the nice easy relamp jobs we get I don't suppose there is much call for LED replacement bulbs on the DR as most of your signals are outside and to be honest I'm not sure whether LU has replacements for the bulbs in LRCL signals yet. On the Picc we changed all the bulbs for LED clusters in the tunnel signal heads and repeaters years ago. In fact I think the Picc led the way in this field and we tried several types of LED cluster before settling for one with the correct sighting and illumination properties. As for relamping, yes much 'work' was lost following the LED replacement programme. Strangely at the west end of the Picc relamp jobs almost always occurred following night signal maintenance by one particular lineman. We discovered that rather than arrange to display aspects to check the bulbs he simply swapped a working bulb from the displayed aspect to the extinguished one and then tested the displaced bulbs in the displayed aspect, changing them if necessary! Obviously disturbing working bulbs in this way weakened them but his laziness was frequently rewarded at 0630 as he was preparing to ready himself for home as he had to take the calls! My habit was to clear and replace or vice versa all signals when doing maintenance or at least arrange for all controlled signals to be cleared in advance from the control room in areas such as Heathrow where I couldn't be in the loop and at the frame simultaneously. It was handy having an auto in the tunnel at 10s points as invariably someone (usually the Pway) would have earthed the track(s) and replaced a signal before I reached them! I suppose such communication would be much easier now that Connect has gone live. Brian
|
|
|
Post by c5 on Nov 8, 2007 1:31:20 GMT
My habit was to clear and replace or vice versa all signals when doing maintenance or at least arrange for all controlled signals to be cleared in advance from the control room Brian Not nowadays, (if your talking about engineering hours) No signals should be cleared, mainly to do with points as there might be staff working there! We do ask the TO to ensure that there is no-one worjing by the points, but of course that's not always possible. I suppose such communication would be much easier now that Connect has gone live. Brian Connect! Not a chance. ;D ;D ;D ;D I doubt it will ever be used by Signal Operators at places like Earls Court and Coburg, there is nowhere for it to go! And it's not very good, better quality sound than the old system though and a choice of ringtones on the hand portables.
|
|
|
Post by railtechnician on Nov 8, 2007 1:37:45 GMT
from what i have seen and heard about LED's in signal heads on LUL it will be only allowed if the LED's was a direct replacement for a bulb (like the type in plat repeaters) I think that's unlikely (though stand corrected on this) there would need to be a lot of work done in development to ensure that the LED cluster and the inner/outer fresnel doublets are compatible. I think that there would be a lot of discussion about making more signals approach lit at red - and changing the sighting lines of heads if you're going to go for the 'searchlight' option in tunnel. Having said that I can see a case for making normally GR 'down' signals LED on the most restrictive aspect and conversely those with the GR (usually) 'up' LED on whatever flavour of 'proceed' - however the use of two different (and both efficient in their own way) lighting systems may cause a lot of coughing amonst certain quarters. plus for us it will be the end to the nice easy relamp jobs we get But think of all the hours involved in re-sighting signals....... Taking all the above into account; As I have stated elsewhere in this thread LU already has LED clusters in tunnel signals. The resighting work was minimal as I recall except for one location which was the W/B starter at Hatton Cross due mostly I believe to the platform lighting which lead to a further development of LED cluster. AFAIK LED tunnel signals have been operating quite successfully for almost 5 years now. I see no reason why a NR type searchlight signal could not be developed to replace LUs LRCLs and SRCLs using LED clusters, after all the basic signal has been in existence for many years and I would expect all the real design work to be directed at the base of the signal post where the LED clusters and beam focussing equipment would be mounted. Approach controlled signalling, suppressed repeaters and indeed suppressed danger aspects are all tried and tested fetures of LU signalling and I can't see any specific reason to change what exists to accommodate LED cluster technology. As for sighting, it is a task like many others in railway work and I would not expect every signal to need to be resighted unless it was changed in which case it would have to be resighted anyway so that is a null point. Brian Brian
|
|
|
Post by c5 on Nov 8, 2007 1:41:36 GMT
There are some customer posters up on the stations going on about LED signals and improving the underground. I think it made a reference to SPADs somehow as well!
Speaking to an NR driver he says they are much better and in a 4 aspect area only 2 aspects are needed.
I can't see too many being installed until the line upgrade signalling work is being done, as a lot of signals will vanish.
|
|
|
Post by railtechnician on Nov 8, 2007 2:06:31 GMT
My habit was to clear and replace or vice versa all signals when doing maintenance or at least arrange for all controlled signals to be cleared in advance from the control room Brian Not nowadays, (if your talking about engineering hours) No signals should be cleared, mainly to do with points as there might be staff working there! We do ask the TO to ensure that there is no-one worjing by the points, but of course that's not always possible. I suppose such communication would be much easier now that Connect has gone live. Brian Connect! Not a chance. ;D ;D ;D ;D I doubt it will ever be used by Signal Operators at places like Earls Court and Coburg, there is nowhere for it to go! And it's not very good, better quality sound than the old system though and a choice of ringtones on the hand portables. This is simply ridiculous, it is impossible to properly maintain signal assets without operating them. Staff working on or about the track are required to be competent, licensed and properly protected by a competent and licensed Protection master familiar with the area in which work is being undertaken. Under the rules no-one should be working around points unless they are clipped and scotched or unless they are being maintained by properly licensed staff. One of the fundamental flaws in the coordination of engineering works (SABRE) is that the people who 'coordinate' the work generally have no idea about how one task will or may impact upon another. As a lineman doing night maintenance I was either in charge of an area that I was maintaining or I was not but I would never sign check certificates for signalling that I was unable to test fully. Quite honestly anyone who signs a safety AWC these days without having performed ALL the necessary checks and tests to ensure compliance with signal standards is cavalier to say the least. It was also my habit to reserve enough time for a full frame test which is a major undertaking at sites like Wembley Park, Arnos Grove and Northfields and almost as bad if having to fully test Acton East and West. On the Connect point I was not thinking about the signal operator at all. In engineering hours the control room was mine if I was the appointed lineman so long as there were no outstanding operating tasks i.e. Train Masters and Possession Masters needing to talk to the signal operator. As a maintenance lineman I would contact my colleague in the control room to clear signals on site for me not the signal operator and similarly when I was in the control room I cleared routes, set up TDs etc for colleagues doing signal maintenance. I also worked the line Controllers TT panel under the prevailing rules and regulations liaising with colleagues testing those assets. In the days before PA, CCTV and Train Radio maintenance was outsourced I would also work on those control room assets liaising as necessary with outside staff observing the necessary restrictions i.e. Noise Abatement. My point regarding comms was rather about liaising with the control room TO. Brian
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Nov 8, 2007 8:27:35 GMT
Connect! Not a chance. ;D ;D ;D ;D I doubt it will ever be used by Signal Operators at places like Earls Court and Coburg, there is nowhere for it to go! And it's not very good, better quality sound than the old system though and a choice of ringtones on the hand portables. Actually the signal operators on the Vic do use connect radio. And although the Northern doesn't have connect yet, the signal operators do have the trunk radio system - and do use it.
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Nov 8, 2007 11:00:43 GMT
the type i was referring to are already being tested and waiting approval for main use are working on the w/b approaching south ken these are all at different hights and so far have not had any objections yet
|
|
|
Post by railtechnician on Nov 8, 2007 16:06:49 GMT
the type i was referring to are already being tested and waiting approval for main use are working on the w/b approaching south ken these are all at different hights and so far have not had any objections yet Well of course the potential drawback to LED clusters in open areas could be sunlight or a weak light source but of course LED clusters have been tried and tested for several years now in such places as the traffic signals at Hanger lane gyratory and seen across London as bus brake lights too. The potential saving in terms of signal maintenance costs must be enormous.
|
|
|
Post by programmes1 on Nov 9, 2007 13:24:51 GMT
Reading all the replies very interesting, but where do LU have LED signals I believe on SSL there are some and on the Central line there is fibre optics but no LED? Reading the reports there still seem to be a large number of spads due to no aspect and the poor T/Op glides past or makes every effort to stop when they have relised they should be stopping due to a danger signal.
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Nov 9, 2007 15:44:27 GMT
On the District we have LED signals (at least, that's what we've been told they are!) approaching South Ken W/B and at Whitechapel (e.g. platforms 2 and 3 starters).
They have one LED cluster to replace each bulb, so there's still coloured glass in the signal head. I believe the LEDs are also coloured so the combination of LED and glass gives an appropriate colour light. They are noticeably brighter in all conditions.
|
|
|
Post by railtechnician on Nov 9, 2007 17:29:14 GMT
Reading all the replies very interesting, but where do LU have LED signals I believe on SSL there are some and on the Central line there is fibre optics but no LED? Reading the reports there still seem to be a large number of spads due to no aspect and the poor T/Op glides past or makes every effort to stop when they have relised they should be stopping due to a danger signal. As I mentioned the Picc has them in the tunnels, LED clusters in standard 4.5" tube signal heads. Brian
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Nov 9, 2007 17:35:51 GMT
if memory serves me right they are called SARL's dont ask me what it stands for it is a direct replacement for the 100v 3pin 33.5w bulbs that we use i put the ones at embankment e/b plat repeater and also victoria w/b plat repeater they are very bright and they are coloured in fact to change them you do need a safety authroity to work certificate (AWC) they are not like the ones used on NR as these replace the lense aswell
|
|
Tom
Administrator
Signalfel?
Posts: 4,196
|
Post by Tom on Nov 11, 2007 13:25:15 GMT
from what i have seen and heard about LED's in signal heads on LUL it will be only allowed if the LED's was a direct replacement for a bulb (like the type in plat repeaters) the ones you are referring too are very big and have lots of ultra bright LED's and there is concern about them being too bright especially down the tunnels plus for us it will be the end to the nice easy relamp jobs we get In fact I think the Picc led the way in this field and we tried several types of LED cluster before settling for one with the correct sighting and illumination properties. ISTR the Picc leading things as well. Pity the final product chosen was non-compliant with a Cat 1 LU standard. ;D [The resighting work was minimal as I recall except for one location which was the W/B starter at Hatton Cross due mostly I believe to the platform lighting which lead to a further development of LED cluster. I know the Jubilee line had a number of problems - some of which were phantom aspects caused by the relationship between the headlights and the signal, and some because the LED cluster had a narrower beam compared to a lamp, which led to reports of dim aspects. EDIT: Oh, and I forgot to mention that any changes to the sighting of a signal should be subjected to a principles test as per LU Standards. if memory serves me right they are called SARL's I think you mean Marl, who are the manufacturer. No complicated abbreviations this time!
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Nov 12, 2007 16:27:54 GMT
thats it well its been a while and i am getting old now my memory is deffo not what it used to be
|
|
|
Post by railtechnician on Nov 13, 2007 3:30:17 GMT
ISTR the Picc leading things as well. Pity the final product chosen was non-compliant with a Cat 1 LU standard. ;D I know the Jubilee line had a number of problems - some of which were phantom aspects caused by the relationship between the headlights and the signal, and some because the LED cluster had a narrower beam compared to a lamp, which led to reports of dim aspects. EDIT: Oh, and I forgot to mention that any changes to the sighting of a signal should be subjected to a principles test as per LU Standards. I think you mean Marl, who are the manufacturer. No complicated abbreviations this time! Yep Marl rings a bell with me! Now what makes you think the LEDs fitted to the Picc tube signal heads were not compliant with signal standards? I hope you don't think we just picked a replacement off the shelf and used it. It was months and months of evaluation, testing and redevelopment as I recall. Just which LU Cat 1 standard might you be referring to? Now just who do you think sights the signals in the first place and do bear in mind that there is a deal of difference between sighting and siting with standards applicable to both and the scale plan too of course! Naturally where siting or sighting is an issue a suitably qualified and appropriately licensed individual will authorise the alterations and a suitably qualified and appropriately licensed individual will make the alterations under a safety AWC. My recollection is that initially LED clusters were trialled at certain signals under an AWC, subsequently following approval LED clusters were simply fitted as replacements as normal routine maintenance. Actually it was the Picc that led the way in changing track circuit fuses as well. Now we ditched nearly all the glass 3 Amp track fuses in favour of Bussman ceramic fuses in an attempt to kill two birds with one stone. Glass fuses are deemed to be a H&S hazard and they seemed to fail easily. Unfortunately after we had changed a great deal of track fuses we discovered that not only had the new fuses not been approved but also that they had an inherent flaw and were less reliable, often fracturing during installation or removal. Track failures actually increased as a result. We then hurriedly ran around like headless chickens replacing all the Bussman fuses with an approved ceramic type, this being the Ferraz fuse. The replacement program meant fitting 2 Amp ceramic fuses instead of 3 Amp and 4 Amp ceramics instead of 5 Amp. This was all occurring at a time when we were changing every trainstop motor for a new much lighter aluminium type and also changing all the point motors and chairlock WLs too. It was a very busy period as I recall.
|
|
Tom
Administrator
Signalfel?
Posts: 4,196
|
Post by Tom on Nov 13, 2007 14:21:00 GMT
E7005 (Wayside Signalling, now a Cat 2 Standard) states: "All running signals using incandescent lamps shall have either a double filament bulb or two blulbs per aspect to enable the train service to continue if one filament or bulb fails. The second filament or bulb should be underrun and act as a standby, should the other one fail. LED Signal Lamp replacements shall incorporate redundant features to achieve the above."
The standard has now been overtaken by 2-01203-004 (which has again been renumbered) but the clause remains in a similar form. On the Marl tube signal LED, the cluster is wired in series such that should a single LED fail open circuit, the whole unit will fail. We wanted to put them in on BCV and had to apply for a concession first.
|
|
|
Post by railtechnician on Nov 14, 2007 5:49:19 GMT
E7005 (Wayside Signalling, now a Cat 2 Standard) states: "All running signals using incandescent lamps shall have either a double filament bulb or two blulbs per aspect to enable the train service to continue if one filament or bulb fails. The second filament or bulb should be underrun and act as a standby, should the other one fail. LED Signal Lamp replacements shall incorporate redundant features to achieve the above." The standard has now been overtaken by 2-01203-004 (which has again been renumbered) but the clause remains in a similar form. On the Marl tube signal LED, the cluster is wired in series such that should a single LED fail open circuit, the whole unit will fail. We wanted to put them in on BCV and had to apply for a concession first. I am surprised at that because I asked the very question regarding redundancy when we were installing the LED clusters and fitting a dummy cap in the standby lampholder. I was told that the LED clusters comprised parallel LED circuits!
|
|
Tom
Administrator
Signalfel?
Posts: 4,196
|
Post by Tom on Nov 15, 2007 0:37:50 GMT
Not according to the data sheet I saw.
I think I might be off Marl's Christmas card list this year!
|
|